Fuse recloser coordination: PE Power Protection practice question
A 12.47 kV feeder recloser uses fuse saving: two fast operations, then two delayed. A lateral tap downstream is protected by an expulsion fuse link. In the current range of interest, the fuse characteristics can be approximated as:
- minimum melting:
- total clearing:
The recloser's fast curve clears in 0.050 s at these currents. To account for fuse heating over the two fast operations, the utility requires the fuse minimum-melt time to be at least 1.35 times the fast-curve clearing time. The highest fault current on the lateral for which fuse saving still works is most nearly: